Power options for an EMC Centera 40U-C

Product:

 

Centera

 

Description:

 

Power options for an EMC Centera 40U-C

 

Resolution:

 

Power distribution contains either:

 

• Two power distribution units (PDUs) and two power distribution panels (PDPs) installed in the lower half of the rack.

 

OR

 

• Four PDUs and four PDPs. Each PDP requires a 30A power cord.  EMC Centera Gen4/Gen4LP in a 40U-C rack

 

Note:

 

EMC recommends that the external power cords of the two  possible PDPs on the left side of the rack be connected to one external power grid and the external power cords of the two possible PDPs on the right side of the rack be connected to a different external power grid for higher availability in the event of power source failures.

 

Power cable options:

 

• Single power inlet cord Option IP-57 Australia (P/N 118032024 or 038-003-439).

• Single power inlet cord Option IEC-309-332P6 International (P/N 118032025 or 038-003-440).

• Single power inlet cord Option with Hubbell L6-30P connector, North America/Japan (P/N 118032023 or 038-003-438).

• Hubbell L6-30R to Russellstoll 3750DP cable (P/N 118032375  or 038-003-441).

 

3-Phase:

 

Two 3-phase power systems are available in the EMC Centera 40U-C rack: North American 3-phase and International 3-phase

 

Power distribution:

 

• Four PDUs and two PDPs.

• North American and International 3-phase requires different power cords because they have different electrical specifications.

 

Note:

 

EMC recommends that the power cords of each PDP are  connected to separate power grids.

 

Power cable options:

 

3-Phase Delta PDP North American power cable options:

 

  • 50A, 3-phase Delta PDP cord, North America, 15', Hubbell connector both ends (8364/8365)
  • 50A, 3-phase Delta PDP cord, North America, 15', (Hubell 8364/Russell Stoll).